The instructions that came with my new EarthX battery had very poor instructions for connecting the BMS lead to my Skyview EMS. Here are the correct configuration settings, which were sent to me by Skyview Tech Support:
1) Connect the EarthX fault monitoring wire to any unused General Purpose input (type = A or C) on the SV-EMS-220. (Pins 4, 7, 8, 9, 10, 11, 12, 20, 21, 22, 23, or 31)
2) Configure the input in the EMS SETUP> SENSOR INPUT MAPPING. FUNCTION = CONTACT, SENSOR = CONTACT, NAME = EARTHX (select CUSTOM and enter a suitable name)
3) Configure the EARTHX CONTACT in EMS SETUP> SESNOR SETUP.
ALARM = SELF-CLEARING
MAXIMUM GRAPHICAL DISPLAY = 5.0 VOLTS
MINIMUM GRAPHICAL DISPLAY = 0.0 VOLTS
RANGE 1
ENABLE = YES
NAME = ALRM
COLOR = RED
TOP = 1.0 VOLTS
BOTTOM = 0.0 VOLTS
RANGE 2
ENABLE = YES
NAME = (NOT SET)
COLOR = BLACK
TOP = 5.0 VOLTS
BOTTOM = 1.0 VOLTS
Ranges 3, 4, and 5: ENABLE = NO
4) Place the EARTHX CONTACT widget on the 100%, 50%, and 20% EMS screens using the EMS-SETUP> SCREEN LAYOUT EDITOR
1) Connect the EarthX fault monitoring wire to any unused General Purpose input (type = A or C) on the SV-EMS-220. (Pins 4, 7, 8, 9, 10, 11, 12, 20, 21, 22, 23, or 31)
2) Configure the input in the EMS SETUP> SENSOR INPUT MAPPING. FUNCTION = CONTACT, SENSOR = CONTACT, NAME = EARTHX (select CUSTOM and enter a suitable name)
3) Configure the EARTHX CONTACT in EMS SETUP> SESNOR SETUP.
ALARM = SELF-CLEARING
MAXIMUM GRAPHICAL DISPLAY = 5.0 VOLTS
MINIMUM GRAPHICAL DISPLAY = 0.0 VOLTS
RANGE 1
ENABLE = YES
NAME = ALRM
COLOR = RED
TOP = 1.0 VOLTS
BOTTOM = 0.0 VOLTS
RANGE 2
ENABLE = YES
NAME = (NOT SET)
COLOR = BLACK
TOP = 5.0 VOLTS
BOTTOM = 1.0 VOLTS
Ranges 3, 4, and 5: ENABLE = NO
4) Place the EARTHX CONTACT widget on the 100%, 50%, and 20% EMS screens using the EMS-SETUP> SCREEN LAYOUT EDITOR