Pitot Heat Indications

paul330

Member
Joined
Mar 10, 2007
Messages
107
I have the Dynon heated pitot/AOA probe and connected up the status wire to the EMS.

With the power off, the indication shows blank/ON. When I switch it on it shows AMBER/OFF. Confused!
 

dlloyd

Member
Joined
Oct 12, 2011
Messages
139
Location
Locust, NC
I changed mine to green on, red off. Might go back and change to amber off. Can be changed in Setup Menu>EMS Setup>Sensor Setup>Pitot Heat.
 

paul330

Member
Joined
Mar 10, 2007
Messages
107
OK, think I have worked this one out. I used the dynon recommended Lycoming 6 set-up but it looks like the pitot is not configured correctly. Found the page in the manual that refers.
 

Dynon

Dynon Staff
Staff member
Joined
Jan 14, 2013
Messages
14,232
Location
Woodinville, WA
We actually labeled it that way with intent, to reflect the way they do it in certified land (caution when off, no caution when on). But you're welcome to change it to suit your preference.
 

paul330

Member
Joined
Mar 10, 2007
Messages
107
I understand that but mine is sensing ON/OFF the wrong way round! With power OFF it indicates on, with power ON it indicates OFF with a caution. I can't see how I could have connected it incorrectly as there is only one wire to connect. I'll look at the sensor set-up at the weekend.
 

paul330

Member
Joined
Mar 10, 2007
Messages
107
Fixed the sensor set-up and now OK. I can't remember whether I initially wrote the code or if it came as default from Dynon on the Lycoming 6 set-up.
 